CS-2 "died" after reboot of PBX

This is the main discussion forum, if the subject that you want to talk about is not listed around here.
dbygnes

CS-2 "died" after reboot of PBX

Post by dbygnes »

Hi

Today I did a reboot of a newly installed OXE r10.0 (common hw) and after that I'm no longer able to get any data out from the config port. I'm also not able to ping it or in any other ways get connected to the CS-2 board. I spoke to a couple of colleagues about this and apparently they have experienced the same thing on two other occasions as well - both resulting in a replacement board. Has anyone of you guys experienced this? I'm doing an install right now for a customer on the opposite of the world, so I'm pretty desperate to know if there are any quick fixes to this problem that I should be aware of.

Thank you very much for any help!
matt

Re: CS-2 "died" after reboot of PBX

Post by matt »

I have had exactly the same problem with 4 x CS-2 boards. Seems to be a bios issue as the board is completely wiped as though the bios does not even start. I have an eSR logged on this issue and will provide further feedback once A-L TS have checked it.
matt

Re: CS-2 "died" after reboot of PBX

Post by matt »

I logged an eSR with A-L and the best they could tell me was that there was a problem with a voltage converter in the CS-2. If you plug it into a small rack-3 it will come up OK and then you can move it back to the large rack but it will die again if you hard boot it in a couple of days. they could not even tell me from what serial number the problem was fixed, just that it had been and I should return the board, but even their"new" board they sent as a replacement has the same issue. I do not think they have fixed the issue at all and there are many boards in production that are 1 hard reboot away from the same failure. :( :( :(
OXE_4400
Member
Posts: 501
Joined: 19 Jul 2007 06:22
Location: Lithuania, Europe

Re: CS-2 "died" after reboot of PBX

Post by OXE_4400 »

I got similar problem, CS-2 starts only in slot 0 ( GD) place, but not in own 2 (small rack). I have replaced cs-2 2 weeks ago and it works. Hope it will work ...
Even after restart. I have restarted a lot of times.
Matt
Do You have any info from eSR like observation sheet number or something similar? O lets say what ind number of board like ACCxxxyyyzzzzz ? Maybe old one too?
OXE_4400
Member
Posts: 501
Joined: 19 Jul 2007 06:22
Location: Lithuania, Europe

Re: CS-2 "died" after reboot of PBX

Post by OXE_4400 »

Symptom:
CS2 board will not come in service when there is a power outage or power unplugged.

Diagnosis:
Please refer the CR crms00345557 (in close/reject tab update found as below). No software modification: Ok But a HW modification is needed;
please see below the R&D HW root cause analysis update:
Root cause: "By analyzing the board, the problem comes from the start of the 1V2 voltage converter (HOST_IO_1V2).
Has been resolved by a FA 3EH73086AAJBFAZZA for the REVISION 09 (ECO-0000068553) of the CS2 board."
OXE_4400
Member
Posts: 501
Joined: 19 Jul 2007 06:22
Location: Lithuania, Europe

Re: CS-2 "died" after reboot of PBX

Post by OXE_4400 »

Another case, 2 reports:
Symptom:
Cs-2 is not booting up with new MR3 cabinet.
Solution:
There is a technical alert about the new cabinet s issue with CS-2 and the same has been corrected from MR3 (3BA00406AB)., hence need to go for RMA to get the faulty cabinets replaced

Symptom:
CS-2 board start -up problem in large cabinet
Diagnosis:
Known issue and it was reported in crms00345557
elkiwi

Re: CS-2 "died" after reboot of PBX

Post by elkiwi »

I have same issue with 3EH73086ABJB rev11 Boards. where can i found crms00345557?? I try with BP but found nothing!!
OXE_4400
Member
Posts: 501
Joined: 19 Jul 2007 06:22
Location: Lithuania, Europe

Re: CS-2 "died" after reboot of PBX

Post by OXE_4400 »

I guess that You can't solve problem yourself. Need to open SR.
elkiwi

Re: CS-2 "died" after reboot of PBX

Post by elkiwi »

Yes, i did it, but they didn´t know if this is a CS-2 issue or a power supply issue. I made a rma A-L send me a new CS-2 and same happens!!
OXE_4400
Member
Posts: 501
Joined: 19 Jul 2007 06:22
Location: Lithuania, Europe

Re: CS-2 "died" after reboot of PBX

Post by OXE_4400 »

Symptom:
CS-2 does not boot up in slot 8 on LARGE RACK
Diagnosis:
Known issue on CS-2 board
Solution:
Fixed in ed 13
1-140482691
======
Solution:
fixed with cs-2 board : "3EH73086ABJB rev13"
1-140940851
=========
Diagnosis:
There is hardware issue happening on all editions of CS-2 boards until edition 11 (3EH73086ABJB 11). The issue is related to a thermal problem.

Solution:
Solution is to do a hardware correction in factory and then the board will take the new edition 13. So replace by 3EH73086ABJB rev13.
Post Reply

Return to “MAIN”