Power input for PCS Cabinet

This is the main discussion forum, if the subject that you want to talk about is not listed around here.
Post Reply
junoooni
Member
Posts: 160
Joined: 29 Aug 2016 02:34

Power input for PCS Cabinet

Post by junoooni »

Hi Experts

I have an OXE with ACT cabinets... PCS is equipped with 4 x rectifiers... as per documentation, each rectifier is 1000W (18.5A)... On site I have power sockets with only 32Amps... since it is 3 x active rectifiers, does that mean my power input should be 64 Amps to handle 18.5x3 = 55.5Amps?

Please share your experience
vad
Alcatel Unleashed Certified Guru
Alcatel Unleashed Certified Guru
Posts: 3806
Joined: 23 Sep 2004 06:47

Re: Power input for PCS Cabinet

Post by vad »

Power consumption f.e. for M3 cabinet (with up to two ACT-28 shelves) must not exceed 26,5 A. Why are you talking about 55,5 A?
User avatar
alex
Senior Member
Posts: 1457
Joined: 06 Jul 2004 07:27
Contact:

Re: Power input for PCS Cabinet

Post by alex »

Man what are talking about exactly?
About 220V AC power or 48V DC power?
Just do simple math:
1000W is the same (roughly) as 54Vx18.5A and 220Vx4.5A.
On AC you need only 4.5Ax3=13.5A for 3 rectifiers active.
If it looks like a duck, swims like a duck, and quacks like a duck, then it probably is a duck.
vad
Alcatel Unleashed Certified Guru
Alcatel Unleashed Certified Guru
Posts: 3806
Joined: 23 Sep 2004 06:47

Re: Power input for PCS Cabinet

Post by vad »

Hi Alex. As I understand TS - he talk about DC.